APC Metered PDU Data source value is showing in Last DS column. Value Column is showing NaN

Post general support questions here that do not specifically fall into the Linux or Windows categories.

Moderators: Developers, Moderators

kjstech
Cacti User
Posts: 97
Joined: Thu Feb 28, 2013 2:57 pm

APC Metered PDU Data source value is showing in Last DS column. Value Column is showing NaN

Post by kjstech »

I'm having a real tough time trying to graph power loads on APC9xxx series metered PDUs.
I have found the OID's for the data I want to graph and they are in data sources. The device is responding to SNMP and the values are retrieved. However in graphs are blank and the only thing I can think of is the value is in the Last DS column not the Value column.

I'm not sure what Last DS even means?
Data Source Template
Data Source Template
datasource-column-mismatch.jpg (305.07 KiB) Viewed 292 times
[attachment=1]datasource-column-mismatch.jpg[happeningent]

Is there any easy way to correct?

This is happening for any of the APC SNMP OID's
APC - Metered PDU Multi-Bank B1 Load .1.3.6.1.4.1.318.1.1.26.8.3.1.5.1
APC - Metered PDU Multi-Bank B1 Low Load Warning Threshold .1.3.6.1.4.1.318.1.1.26.8.1.1.5.1
APC - Metered PDU Multi-Bank B1 Near Overload Warning Threshold .1.3.6.1.4.1.318.1.1.26.8.1.1.6.1
APC - Metered PDU Multi-Bank B1 Overload Alarm Threshold .1.3.6.1.4.1.318.1.1.26.8.1.1.7.1

APC - Metered PDU Multi-Bank B2 Load .1.3.6.1.4.1.318.1.1.26.8.3.1.5.2
APC - Metered PDU Multi-Bank B2 Low Load Warning Threshold .1.3.6.1.4.1.318.1.1.26.8.1.1.5.2
APC - Metered PDU Multi-Bank B2 Near Overload Warning Threshold .1.3.6.1.4.1.318.1.1.26.8.1.1.6.2
APC - Metered PDU Multi-Bank B2 Overload Alarm Threshold .1.3.6.1.4.1.318.1.1.26.8.1.1.7.2

APC - Metered PDU Multi-Bank Total Load .1.3.6.1.4.1.318.1.1.26.6.3.1.5.1
APC - Metered PDU Multi-Bank Total Low Load Warning Threshold .1.3.6.1.4.1.318.1.1.26.6.1.1.5.1
APC - Metered PDU Multi-Bank Total Near Overload Warning Threshold .1.3.6.1.4.1.318.1.1.26.6.1.1.6.1
APC - Metered PDU Multi-Bank Total Overload Alarm Threshold .1.3.6.1.4.1.318.1.1.26.6.1.1.7.1
Attachments
Data Source
Data Source
Data source template example.jpg (222.35 KiB) Viewed 292 times
macan
Cacti Pro User
Posts: 898
Joined: Tue Mar 18, 2008 2:30 am
Location: Czech

Re: APC Metered PDU Data source value is showing in Last DS column. Value Column is showing NaN

Post by macan »

try from cacti host:
snmpget -c your_community -v your_snmp_version IP .1.3.6.1.4.1.318.1.1.26.8.3.1.5.1
Will you get correct answer?
Let the Cacti grow!
kjstech
Cacti User
Posts: 97
Joined: Thu Feb 28, 2013 2:57 pm

Re: APC Metered PDU Data source value is showing in Last DS column. Value Column is showing NaN

Post by kjstech »

Using manage engine mibbrowser yes, I get the correct value (cdef will divide that by 10 to get amps).

Its the same value cacti shows in the last DS column.
apc-mib.jpg
apc-mib.jpg (199.55 KiB) Viewed 273 times
macan
Cacti Pro User
Posts: 898
Joined: Tue Mar 18, 2008 2:30 am
Location: Czech

Re: APC Metered PDU Data source value is showing in Last DS column. Value Column is showing NaN

Post by macan »

we have template APC_InfraStruXure_PDU.xml which contains your OID. You can try it.
It was added in 1.2.25 or 1.2.26.
Try to install:
php path/to/cacti/cli/import_package.php --filename=APC_InfraStruXure_PDU.xml.gz
Let the Cacti grow!
kjstech
Cacti User
Posts: 97
Joined: Thu Feb 28, 2013 2:57 pm

Re: APC Metered PDU Data source value is showing in Last DS column. Value Column is showing NaN

Post by kjstech »

Ok when I do that, I see it claims sucess adding these graph templates:
Graph Template
[success] APC PDU - System Output Neutral Current [new]
[success] APC PDU - System Output Frequency [new]
[success] APC PDU - System Output Total Apparent Power [new]
[success] APC PDU - System Output Total Power [new]
[success] APC PDU - System Output Total Power Factor [new]
[success] APC PDU - Branch Breaker Current [new]
[success] APC PDU - Main Input Phase Voltage [new]
[success] APC PDU - System Output Phase Voltage (L-L) [new]
[success] APC PDU - System Output Phase Voltage (L-N) [new]
[success] APC PDU - System Output Phase Current [new]
[success] APC PDU - System Output Phase Power [new]
[success] APC PDU - System Output Phase Apparent Power [new]
[success] APC PDU - System Output Phase Power Factor [new]

But none of those are selectable if I try to add additional graph template names to the device. What am I doing wrong? Just the old ones are in there.
apc pdu cacti issues.jpg
apc pdu cacti issues.jpg (176.33 KiB) Viewed 258 times
kjstech
Cacti User
Posts: 97
Joined: Thu Feb 28, 2013 2:57 pm

Re: APC Metered PDU Data source value is showing in Last DS column. Value Column is showing NaN

Post by kjstech »

No I dont think that xml works either. APC = PDU - Phase statistics retunrs 0 items/rows

Total: 0.000000, Delta: 0.000000, Found data query XML file at '/var/www/html/cacti/resource/snmp_queries/apc_pdu_phases.xml'
Total: 0.000000, Delta: 0.000000, Running Data Query [41].
Total: 0.000000, Delta: 0.000000, Found Type = '3' [SNMP Query].
Total: 0.000000, Delta: 0.000000, XML file parsed ok.
Total: 0.000000, Delta: 0.000000, Auto Bulk Walk Size Selected.
Total: 0.020000, Delta: 0.020000, Tested Bulk Walk Size 1 with a response of 0.0085.
Total: 0.040000, Delta: 0.020000, Tested Bulk Walk Size 5 with a response of 0.0020.
Total: 0.050000, Delta: 0.020000, Tested Bulk Walk Size 10 with a response of 0.0020.
Total: 0.050000, Delta: 0.000000, Bulk Walk Size selected was 5.
Total: 0.060000, Delta: 0.000000, Executing SNMP get for num of indexes @ '1' Index Count:
Total: 0.060000, Delta: 0.000000, Executing SNMP walk for list of indexes @ '.1.3.6.1.2.1.7.2' Index Count: 1
Total: 0.060000, Delta: 0.000000, Index found at OID: '.1.3.6.1.2.1.7.2.0' value: '20985'
Total: 0.060000, Delta: 0.000000, Filtering list of indexes @ '.1.3.6.1.2.1.7.2' Index Count: 0
Total: 0.060000, Delta: 0.000000, Located input field 'IdentProductName' [get]
Total: 0.060000, Delta: 0.000000, Checking for Sort Field change. No changes detected.
Total: 0.060000, Delta: 0.000000, Update Data Query Sort Cache complete
Total: 0.060000, Delta: 0.000000, Index Association with Local Data complete
Total: 0.070000, Delta: 0.020000, No Index Changes Detected, Skipping Re-Index and Poller Cache Re-population
Total: 0.070000, Delta: 0.000000, Automation Executing for Data Query complete
Total: 0.070000, Delta: 0.000000, Plugin hooks complete
macan
Cacti Pro User
Posts: 898
Joined: Tue Mar 18, 2008 2:30 am
Location: Czech

Re: APC Metered PDU Data source value is showing in Last DS column. Value Column is showing NaN

Post by macan »

kjstech wrote: Wed May 08, 2024 12:38 pm Ok when I do that, I see it claims sucess adding these graph templates:
Graph Template
[success] APC PDU - System Output Neutral Current [new]
[success] APC PDU - System Output Frequency [new]
[success] APC PDU - System Output Total Apparent Power [new]
[success] APC PDU - System Output Total Power [new]
[success] APC PDU - System Output Total Power Factor [new]
[success] APC PDU - Branch Breaker Current [new]
[success] APC PDU - Main Input Phase Voltage [new]
[success] APC PDU - System Output Phase Voltage (L-L) [new]
[success] APC PDU - System Output Phase Voltage (L-N) [new]
[success] APC PDU - System Output Phase Current [new]
[success] APC PDU - System Output Phase Power [new]
[success] APC PDU - System Output Phase Apparent Power [new]
[success] APC PDU - System Output Phase Power Factor [new]

But none of those are selectable if I try to add additional graph template names to the device. What am I doing wrong? Just the old ones are in there.

apc pdu cacti issues.jpg
create new device and set device template to APC infrastructure ....
Let the Cacti grow!
macan
Cacti Pro User
Posts: 898
Joined: Tue Mar 18, 2008 2:30 am
Location: Czech

Re: APC Metered PDU Data source value is showing in Last DS column. Value Column is showing NaN

Post by macan »

kjstech wrote: Wed May 08, 2024 12:43 pm No I dont think that xml works either. APC = PDU - Phase statistics retunrs 0 items/rows

Total: 0.000000, Delta: 0.000000, Found data query XML file at '/var/www/html/cacti/resource/snmp_queries/apc_pdu_phases.xml'
Total: 0.000000, Delta: 0.000000, Running Data Query [41].
Total: 0.000000, Delta: 0.000000, Found Type = '3' [SNMP Query].
Total: 0.000000, Delta: 0.000000, XML file parsed ok.
Total: 0.000000, Delta: 0.000000, Auto Bulk Walk Size Selected.
Total: 0.020000, Delta: 0.020000, Tested Bulk Walk Size 1 with a response of 0.0085.
Total: 0.040000, Delta: 0.020000, Tested Bulk Walk Size 5 with a response of 0.0020.
Total: 0.050000, Delta: 0.020000, Tested Bulk Walk Size 10 with a response of 0.0020.
Total: 0.050000, Delta: 0.000000, Bulk Walk Size selected was 5.
Total: 0.060000, Delta: 0.000000, Executing SNMP get for num of indexes @ '1' Index Count:
Total: 0.060000, Delta: 0.000000, Executing SNMP walk for list of indexes @ '.1.3.6.1.2.1.7.2' Index Count: 1
Total: 0.060000, Delta: 0.000000, Index found at OID: '.1.3.6.1.2.1.7.2.0' value: '20985'
Total: 0.060000, Delta: 0.000000, Filtering list of indexes @ '.1.3.6.1.2.1.7.2' Index Count: 0
Total: 0.060000, Delta: 0.000000, Located input field 'IdentProductName' [get]
Total: 0.060000, Delta: 0.000000, Checking for Sort Field change. No changes detected.
Total: 0.060000, Delta: 0.000000, Update Data Query Sort Cache complete
Total: 0.060000, Delta: 0.000000, Index Association with Local Data complete
Total: 0.070000, Delta: 0.020000, No Index Changes Detected, Skipping Re-Index and Poller Cache Re-population
Total: 0.070000, Delta: 0.000000, Automation Executing for Data Query complete
Total: 0.070000, Delta: 0.000000, Plugin hooks complete
Oh, sorry. I got the wrong OID. So return to your original query.
Try to enable device debug and show log
Let the Cacti grow!
kjstech
Cacti User
Posts: 97
Joined: Thu Feb 28, 2013 2:57 pm

Re: APC Metered PDU Data source value is showing in Last DS column. Value Column is showing NaN

Post by kjstech »

Many have numbers, im not sure what to do, Im at a loss.

This is cacti.log filtered for the term apc.

What else can I gather?
2024/05/13 14:28:01 - SPINE: Poller[1] PID[904608] PT[139878979462720] Device[111] HT[1] DS[6777] TT[9.85] SNMP: v3: 10.10.2.1, dsname: apc_single_load, oid: .1.3.6.1.4.1.318.1.1.12.2.3.1.1.2.1, value: 167
2024/05/13 14:28:01 - SPINE: Poller[1] PID[904608] PT[139878979462720] Device[111] HT[1] DS[6729] TT[5.65] SNMP: v3: 10.10.2.1, dsname: apc_bankb1_near, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.6.1, value: 13
2024/05/13 14:28:01 - SPINE: Poller[1] PID[904608] PT[139878979462720] Device[111] HT[1] DS[6712] TT[4.92] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:27:31 - SPINE: Poller[1] PID[904522] PT[140109297641024] Device[111] HT[1] DS[6776] TT[10.47] SNMP: v3: 10.10.2.1, dsname: apc_single_overload, oid: .1.3.6.1.4.1.318.1.1.12.2.2.1.1.4.1, value: 24
2024/05/13 14:27:31 - SPINE: Poller[1] PID[904522] PT[140109297641024] Device[111] HT[1] DS[6728] TT[6.76] SNMP: v3: 10.10.2.1, dsname: apc_bankb1_low, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.5.1, value: 0
2024/05/13 14:27:31 - SPINE: Poller[1] PID[904522] PT[140109297641024] Device[111] HT[1] DS[6711] TT[6.16] SNMP: v3: 10.10.2.1, dsname: APC_line_voltage, oid: .1.3.6.1.4.1.318.1.1.26.6.3.1.6.1, value: 204
2024/05/13 14:27:31 - SPINE: Poller[1] PID[904522] PT[140109297641024] Device[111] HT[1] DS[6702] TT[5.49] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:27:01 - SPINE: Poller[1] PID[904449] PT[140186302649920] Device[111] HT[1] DS[6775] TT[2.51] SNMP: v3: 10.10.2.1, dsname: apc_single_near, oid: .1.3.6.1.4.1.318.1.1.12.2.2.1.1.3.1, value: 19
2024/05/13 14:27:01 - SPINE: Poller[1] PID[904449] PT[140186302649920] Device[111] HT[1] DS[6741] TT[8.18] SNMP: v3: 10.10.2.1, dsname: apc_total_overload, oid: .1.3.6.1.4.1.318.1.1.26.6.1.1.7.1, value: 24
2024/05/13 14:27:01 - SPINE: Poller[1] PID[904449] PT[140186302649920] Device[111] HT[1] DS[6727] TT[7.55] SNMP: v3: 10.10.2.1, dsname: apc_bankb1_load, oid: .1.3.6.1.4.1.318.1.1.26.8.3.1.5.1, value: 65
2024/05/13 14:27:01 - SPINE: Poller[1] PID[904449] PT[140186302649920] Device[111] HT[1] DS[6712] TT[6.90] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:27:01 - SPINE: Poller[1] PID[904449] PT[140186302649920] Device[111] HT[1] DS[6700] TT[6.27] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_overload, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.7.2, value: 16
2024/05/13 14:27:01 - SPINE: Poller[1] PID[904449] PT[140186302649920] Device[111] HT[1] DS[6699] TT[5.64] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_near, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.6.2, value: 13
2024/05/13 14:27:01 - SPINE: Poller[1] PID[904449] PT[140186302649920] Device[111] HT[1] DS[6697] TT[4.93] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_load, oid: .1.3.6.1.4.1.318.1.1.26.8.3.1.5.2, value: 108
2024/05/13 14:26:31 - SPINE: Poller[1] PID[904362] PT[140518109476416] Device[111] HT[1] DS[6774] TT[8.19] SNMP: v3: 10.10.2.1, dsname: apc_single_low, oid: .1.3.6.1.4.1.318.1.1.12.2.2.1.1.2.1, value: 0
2024/05/13 14:26:31 - SPINE: Poller[1] PID[904362] PT[140518109476416] Device[111] HT[1] DS[6740] TT[4.40] SNMP: v3: 10.10.2.1, dsname: apc_total_low, oid: .1.3.6.1.4.1.318.1.1.26.6.1.1.5.1, value: 0
2024/05/13 14:26:31 - SPINE: Poller[1] PID[904362] PT[140518109476416] Device[111] HT[1] DS[6702] TT[3.71] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:26:01 - SPINE: Poller[1] PID[904289] PT[139768626325056] Device[111] HT[1] DS[6739] TT[6.15] SNMP: v3: 10.10.2.1, dsname: apc_total_load, oid: .1.3.6.1.4.1.318.1.1.26.6.3.1.5.1, value: 165
2024/05/13 14:26:01 - SPINE: Poller[1] PID[904289] PT[139768626325056] Device[111] HT[1] DS[6712] TT[5.51] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:26:01 - SPINE: Poller[1] PID[904289] PT[139768626325056] Device[111] HT[1] DS[6698] TT[4.86] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_low, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.5.2, value: 0
2024/05/13 14:26:01 - SPINE: Poller[1] PID[904289] PT[139768626325056] Device[111] HT[1] DS[6696] TT[3.91] SNMP: v3: 10.10.2.1, dsname: apc_bankb1_overload, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.7.1, value: 16
2024/05/13 14:25:31 - SPINE: Poller[1] PID[904201] PT[140550033782336] Device[111] HT[1] DS[6738] TT[6.22] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_overload, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.7.2, value: 16
2024/05/13 14:25:31 - SPINE: Poller[1] PID[904201] PT[140550033782336] Device[111] HT[1] DS[6734] TT[5.70] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_overload, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.7.2, value: 16
2024/05/13 14:25:31 - SPINE: Poller[1] PID[904201] PT[140550033782336] Device[111] HT[1] DS[6702] TT[5.07] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:25:01 - SPINE: Poller[1] PID[904130] PT[139914037626432] Device[111] HT[1] DS[6737] TT[4.94] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_near, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.6.2, value: 13
2024/05/13 14:25:01 - SPINE: Poller[1] PID[904130] PT[139914037626432] Device[111] HT[1] DS[6733] TT[4.26] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_near, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.6.2, value: 13
2024/05/13 14:25:01 - SPINE: Poller[1] PID[904130] PT[139914037626432] Device[111] HT[1] DS[6712] TT[3.49] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:24:31 - SPINE: Poller[1] PID[904042] PT[140596974749248] Device[111] HT[1] DS[6736] TT[6.00] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_low, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.5.2, value: 0
2024/05/13 14:24:31 - SPINE: Poller[1] PID[904042] PT[140596974749248] Device[111] HT[1] DS[6732] TT[5.03] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_low, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.5.2, value: 0
2024/05/13 14:24:31 - SPINE: Poller[1] PID[904042] PT[140596974749248] Device[111] HT[1] DS[6702] TT[3.89] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:24:01 - SPINE: Poller[1] PID[903972] PT[140219654788672] Device[111] HT[1] DS[6735] TT[5.33] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_load, oid: .1.3.6.1.4.1.318.1.1.26.8.3.1.5.2, value: 107
2024/05/13 14:24:01 - SPINE: Poller[1] PID[903972] PT[140219654788672] Device[111] HT[1] DS[6731] TT[4.60] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_load, oid: .1.3.6.1.4.1.318.1.1.26.8.3.1.5.2, value: 107
2024/05/13 14:24:01 - SPINE: Poller[1] PID[903972] PT[140219654788672] Device[111] HT[1] DS[6712] TT[3.66] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:23:31 - SPINE: Poller[1] PID[903885] PT[140075727849024] Device[111] HT[1] DS[6730] TT[4.42] SNMP: v3: 10.10.2.1, dsname: apc_bankb1_overload, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.7.1, value: 16
2024/05/13 14:23:31 - SPINE: Poller[1] PID[903885] PT[140075727849024] Device[111] HT[1] DS[6702] TT[3.86] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:23:31 - SPINE: Poller[1] PID[903885] PT[140075727849024] Device[111] HT[1] DS[6695] TT[3.27] SNMP: v3: 10.10.2.1, dsname: apc_bankb1_near, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.6.1, value: 13
2024/05/13 14:23:01 - SPINE: Poller[1] PID[903814] PT[139834768131648] Device[111] HT[1] DS[6777] TT[9.02] SNMP: v3: 10.10.2.1, dsname: apc_single_load, oid: .1.3.6.1.4.1.318.1.1.12.2.3.1.1.2.1, value: 171
2024/05/13 14:23:01 - SPINE: Poller[1] PID[903814] PT[139834768131648] Device[111] HT[1] DS[6729] TT[4.64] SNMP: v3: 10.10.2.1, dsname: apc_bankb1_near, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.6.1, value: 13
2024/05/13 14:23:01 - SPINE: Poller[1] PID[903814] PT[139834768131648] Device[111] HT[1] DS[6712] TT[3.82] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:22:31 - SPINE: Poller[1] PID[903727] PT[140332742440512] Device[111] HT[1] DS[6776] TT[18.93] SNMP: v3: 10.10.2.1, dsname: apc_single_overload, oid: .1.3.6.1.4.1.318.1.1.12.2.2.1.1.4.1, value: 24
2024/05/13 14:22:31 - SPINE: Poller[1] PID[903727] PT[140332742440512] Device[111] HT[1] DS[6728] TT[15.62] SNMP: v3: 10.10.2.1, dsname: apc_bankb1_low, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.5.1, value: 0
2024/05/13 14:22:31 - SPINE: Poller[1] PID[903727] PT[140332742440512] Device[111] HT[1] DS[6711] TT[15.03] SNMP: v3: 10.10.2.1, dsname: APC_line_voltage, oid: .1.3.6.1.4.1.318.1.1.26.6.3.1.6.1, value: 204
2024/05/13 14:22:31 - SPINE: Poller[1] PID[903727] PT[140332742440512] Device[111] HT[1] DS[6702] TT[3.97] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:22:01 - SPINE: Poller[1] PID[903654] PT[140166212220480] Device[111] HT[1] DS[6775] TT[9.03] SNMP: v3: 10.10.2.1, dsname: apc_single_near, oid: .1.3.6.1.4.1.318.1.1.12.2.2.1.1.3.1, value: 19
2024/05/13 14:22:01 - SPINE: Poller[1] PID[903654] PT[140166212220480] Device[111] HT[1] DS[6741] TT[7.82] SNMP: v3: 10.10.2.1, dsname: apc_total_overload, oid: .1.3.6.1.4.1.318.1.1.26.6.1.1.7.1, value: 24
2024/05/13 14:22:01 - SPINE: Poller[1] PID[903654] PT[140166212220480] Device[111] HT[1] DS[6727] TT[7.19] SNMP: v3: 10.10.2.1, dsname: apc_bankb1_load, oid: .1.3.6.1.4.1.318.1.1.26.8.3.1.5.1, value: 65
2024/05/13 14:22:01 - SPINE: Poller[1] PID[903654] PT[140166212220480] Device[111] HT[1] DS[6712] TT[6.49] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:22:01 - SPINE: Poller[1] PID[903654] PT[140166212220480] Device[111] HT[1] DS[6700] TT[5.85] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_overload, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.7.2, value: 16
2024/05/13 14:22:01 - SPINE: Poller[1] PID[903654] PT[140166212220480] Device[111] HT[1] DS[6699] TT[5.21] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_near, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.6.2, value: 13
2024/05/13 14:22:01 - SPINE: Poller[1] PID[903654] PT[140166212220480] Device[111] HT[1] DS[6697] TT[4.47] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_load, oid: .1.3.6.1.4.1.318.1.1.26.8.3.1.5.2, value: 108
2024/05/13 14:21:31 - SPINE: Poller[1] PID[903568] PT[139624583714368] Device[111] HT[1] DS[6774] TT[7.51] SNMP: v3: 10.10.2.1, dsname: apc_single_low, oid: .1.3.6.1.4.1.318.1.1.12.2.2.1.1.2.1, value: 0
2024/05/13 14:21:31 - SPINE: Poller[1] PID[903568] PT[139624583714368] Device[111] HT[1] DS[6740] TT[4.15] SNMP: v3: 10.10.2.1, dsname: apc_total_low, oid: .1.3.6.1.4.1.318.1.1.26.6.1.1.5.1, value: 0
2024/05/13 14:21:31 - SPINE: Poller[1] PID[903568] PT[139624583714368] Device[111] HT[1] DS[6702] TT[3.25] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:21:01 - SPINE: Poller[1] PID[903496] PT[139722634683968] Device[111] HT[1] DS[6739] TT[12.86] SNMP: v3: 10.10.2.1, dsname: apc_total_load, oid: .1.3.6.1.4.1.318.1.1.26.6.3.1.5.1, value: 179
2024/05/13 14:21:01 - SPINE: Poller[1] PID[903496] PT[139722634683968] Device[111] HT[1] DS[6712] TT[12.08] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:21:01 - SPINE: Poller[1] PID[903496] PT[139722634683968] Device[111] HT[1] DS[6698] TT[10.90] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_low, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.5.2, value: 0
2024/05/13 14:21:01 - SPINE: Poller[1] PID[903496] PT[139722634683968] Device[111] HT[1] DS[6696] TT[9.88] SNMP: v3: 10.10.2.1, dsname: apc_bankb1_overload, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.7.1, value: 16
2024/05/13 14:20:31 - SPINE: Poller[1] PID[903407] PT[140635941901888] Device[111] HT[1] DS[6738] TT[5.91] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_overload, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.7.2, value: 16
2024/05/13 14:20:31 - SPINE: Poller[1] PID[903407] PT[140635941901888] Device[111] HT[1] DS[6734] TT[4.62] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_overload, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.7.2, value: 16
2024/05/13 14:20:31 - SPINE: Poller[1] PID[903407] PT[140635941901888] Device[111] HT[1] DS[6702] TT[3.72] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:20:01 - SPINE: Poller[1] PID[903333] PT[140600713950784] Device[111] HT[1] DS[6737] TT[22.04] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_near, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.6.2, value: 13
2024/05/13 14:20:01 - SPINE: Poller[1] PID[903333] PT[140600713950784] Device[111] HT[1] DS[6733] TT[20.85] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_near, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.6.2, value: 13
2024/05/13 14:20:01 - SPINE: Poller[1] PID[903333] PT[140600713950784] Device[111] HT[1] DS[6712] TT[19.77] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:19:31 - SPINE: Poller[1] PID[903248] PT[140375123686976] Device[111] HT[1] DS[6736] TT[19.88] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_low, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.5.2, value: 0
2024/05/13 14:19:31 - SPINE: Poller[1] PID[903248] PT[140375123686976] Device[111] HT[1] DS[6732] TT[18.75] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_low, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.5.2, value: 0
2024/05/13 14:19:31 - SPINE: Poller[1] PID[903248] PT[140375123686976] Device[111] HT[1] DS[6702] TT[16.97] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:19:01 - SPINE: Poller[1] PID[903175] PT[140572159231552] Device[111] HT[1] DS[6735] TT[20.38] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_load, oid: .1.3.6.1.4.1.318.1.1.26.8.3.1.5.2, value: 121
2024/05/13 14:19:01 - SPINE: Poller[1] PID[903175] PT[140572159231552] Device[111] HT[1] DS[6731] TT[17.95] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_load, oid: .1.3.6.1.4.1.318.1.1.26.8.3.1.5.2, value: 121
2024/05/13 14:19:01 - SPINE: Poller[1] PID[903175] PT[140572159231552] Device[111] HT[1] DS[6712] TT[16.09] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:18:31 - SPINE: Poller[1] PID[903092] PT[140252341306944] Device[111] HT[1] DS[6730] TT[6.34] SNMP: v3: 10.10.2.1, dsname: apc_bankb1_overload, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.7.1, value: 16
2024/05/13 14:18:31 - SPINE: Poller[1] PID[903092] PT[140252341306944] Device[111] HT[1] DS[6702] TT[5.51] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:18:31 - SPINE: Poller[1] PID[903092] PT[140252341306944] Device[111] HT[1] DS[6695] TT[4.79] SNMP: v3: 10.10.2.1, dsname: apc_bankb1_near, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.6.1, value: 13
2024/05/13 14:18:01 - SPINE: Poller[1] PID[903018] PT[140708831540800] Device[111] HT[1] DS[6777] TT[9.53] SNMP: v3: 10.10.2.1, dsname: apc_single_load, oid: .1.3.6.1.4.1.318.1.1.12.2.3.1.1.2.1, value: 168
2024/05/13 14:18:01 - SPINE: Poller[1] PID[903018] PT[140708831540800] Device[111] HT[1] DS[6729] TT[5.36] SNMP: v3: 10.10.2.1, dsname: apc_bankb1_near, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.6.1, value: 13
2024/05/13 14:18:01 - SPINE: Poller[1] PID[903018] PT[140708831540800] Device[111] HT[1] DS[6712] TT[4.57] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:17:31 - SPINE: Poller[1] PID[902935] PT[140543476627008] Device[111] HT[1] DS[6776] TT[12.26] SNMP: v3: 10.10.2.1, dsname: apc_single_overload, oid: .1.3.6.1.4.1.318.1.1.12.2.2.1.1.4.1, value: 24
2024/05/13 14:17:31 - SPINE: Poller[1] PID[902935] PT[140543476627008] Device[111] HT[1] DS[6728] TT[8.84] SNMP: v3: 10.10.2.1, dsname: apc_bankb1_low, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.5.1, value: 0
2024/05/13 14:17:31 - SPINE: Poller[1] PID[902935] PT[140543476627008] Device[111] HT[1] DS[6711] TT[8.29] SNMP: v3: 10.10.2.1, dsname: APC_line_voltage, oid: .1.3.6.1.4.1.318.1.1.26.6.3.1.6.1, value: 204
2024/05/13 14:17:31 - SPINE: Poller[1] PID[902935] PT[140543476627008] Device[111] HT[1] DS[6702] TT[7.65] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:17:01 - SPINE: Poller[1] PID[902855] PT[140693753054784] Device[111] HT[1] DS[6775] TT[34.63] SNMP: v3: 10.10.2.1, dsname: apc_single_near, oid: .1.3.6.1.4.1.318.1.1.12.2.2.1.1.3.1, value: 19
2024/05/13 14:17:01 - SPINE: Poller[1] PID[902855] PT[140693753054784] Device[111] HT[1] DS[6741] TT[21.20] SNMP: v3: 10.10.2.1, dsname: apc_total_overload, oid: .1.3.6.1.4.1.318.1.1.26.6.1.1.7.1, value: 24
2024/05/13 14:17:01 - SPINE: Poller[1] PID[902855] PT[140693753054784] Device[111] HT[1] DS[6727] TT[19.56] SNMP: v3: 10.10.2.1, dsname: apc_bankb1_load, oid: .1.3.6.1.4.1.318.1.1.26.8.3.1.5.1, value: 66
2024/05/13 14:17:01 - SPINE: Poller[1] PID[902855] PT[140693753054784] Device[111] HT[1] DS[6712] TT[18.86] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:17:01 - SPINE: Poller[1] PID[902855] PT[140693753054784] Device[111] HT[1] DS[6700] TT[17.17] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_overload, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.7.2, value: 16
2024/05/13 14:17:01 - SPINE: Poller[1] PID[902855] PT[140693753054784] Device[111] HT[1] DS[6699] TT[5.21] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_near, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.6.2, value: 13
2024/05/13 14:17:01 - SPINE: Poller[1] PID[902855] PT[140693753054784] Device[111] HT[1] DS[6697] TT[4.33] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_load, oid: .1.3.6.1.4.1.318.1.1.26.8.3.1.5.2, value: 111
2024/05/13 14:16:31 - SPINE: Poller[1] PID[902772] PT[140598149989952] Device[111] HT[1] DS[6774] TT[10.93] SNMP: v3: 10.10.2.1, dsname: apc_single_low, oid: .1.3.6.1.4.1.318.1.1.12.2.2.1.1.2.1, value: 0
2024/05/13 14:16:31 - SPINE: Poller[1] PID[902772] PT[140598149989952] Device[111] HT[1] DS[6740] TT[7.37] SNMP: v3: 10.10.2.1, dsname: apc_total_low, oid: .1.3.6.1.4.1.318.1.1.26.6.1.1.5.1, value: 0
2024/05/13 14:16:31 - SPINE: Poller[1] PID[902772] PT[140598149989952] Device[111] HT[1] DS[6702] TT[6.69] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:16:01 - SPINE: Poller[1] PID[902696] PT[140044500567616] Device[111] HT[1] DS[6739] TT[5.57] SNMP: v3: 10.10.2.1, dsname: apc_total_load, oid: .1.3.6.1.4.1.318.1.1.26.6.3.1.5.1, value: 166
2024/05/13 14:16:01 - SPINE: Poller[1] PID[902696] PT[140044500567616] Device[111] HT[1] DS[6712] TT[4.77] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:16:01 - SPINE: Poller[1] PID[902696] PT[140044500567616] Device[111] HT[1] DS[6698] TT[4.27] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_low, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.5.2, value: 0
2024/05/13 14:16:01 - SPINE: Poller[1] PID[902696] PT[140044500567616] Device[111] HT[1] DS[6696] TT[3.72] SNMP: v3: 10.10.2.1, dsname: apc_bankb1_overload, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.7.1, value: 16
2024/05/13 14:15:31 - SPINE: Poller[1] PID[902612] PT[140092773496384] Device[111] HT[1] DS[6738] TT[5.55] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_overload, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.7.2, value: 16
2024/05/13 14:15:31 - SPINE: Poller[1] PID[902612] PT[140092773496384] Device[111] HT[1] DS[6734] TT[4.66] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_overload, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.7.2, value: 16
2024/05/13 14:15:31 - SPINE: Poller[1] PID[902612] PT[140092773496384] Device[111] HT[1] DS[6702] TT[3.55] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:15:01 - SPINE: Poller[1] PID[902538] PT[140606056674880] Device[111] HT[1] DS[6737] TT[5.29] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_near, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.6.2, value: 13
2024/05/13 14:15:01 - SPINE: Poller[1] PID[902538] PT[140606056674880] Device[111] HT[1] DS[6733] TT[4.58] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_near, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.6.2, value: 13
2024/05/13 14:15:01 - SPINE: Poller[1] PID[902538] PT[140606056674880] Device[111] HT[1] DS[6712] TT[3.73] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:14:31 - SPINE: Poller[1] PID[902436] PT[140236188485184] Device[111] HT[1] DS[6736] TT[5.90] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_low, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.5.2, value: 0
2024/05/13 14:14:31 - SPINE: Poller[1] PID[902436] PT[140236188485184] Device[111] HT[1] DS[6732] TT[4.78] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_low, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.5.2, value: 0
2024/05/13 14:14:31 - SPINE: Poller[1] PID[902436] PT[140236188485184] Device[111] HT[1] DS[6702] TT[3.86] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:14:01 - SPINE: Poller[1] PID[902366] PT[140690040694336] Device[111] HT[1] DS[6735] TT[5.18] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_load, oid: .1.3.6.1.4.1.318.1.1.26.8.3.1.5.2, value: 110
2024/05/13 14:14:01 - SPINE: Poller[1] PID[902366] PT[140690040694336] Device[111] HT[1] DS[6731] TT[4.48] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_load, oid: .1.3.6.1.4.1.318.1.1.26.8.3.1.5.2, value: 110
2024/05/13 14:14:01 - SPINE: Poller[1] PID[902366] PT[140690040694336] Device[111] HT[1] DS[6712] TT[3.67] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:13:31 - SPINE: Poller[1] PID[902279] PT[139711454135872] Device[111] HT[1] DS[6730] TT[4.78] SNMP: v3: 10.10.2.1, dsname: apc_bankb1_overload, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.7.1, value: 16
2024/05/13 14:13:31 - SPINE: Poller[1] PID[902279] PT[139711454135872] Device[111] HT[1] DS[6702] TT[4.15] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:13:31 - SPINE: Poller[1] PID[902279] PT[139711454135872] Device[111] HT[1] DS[6695] TT[3.46] SNMP: v3: 10.10.2.1, dsname: apc_bankb1_near, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.6.1, value: 13
2024/05/13 14:13:01 - SPINE: Poller[1] PID[902208] PT[140550813124160] Device[111] HT[1] DS[6777] TT[8.53] SNMP: v3: 10.10.2.1, dsname: apc_single_load, oid: .1.3.6.1.4.1.318.1.1.12.2.3.1.1.2.1, value: 173
2024/05/13 14:13:01 - SPINE: Poller[1] PID[902208] PT[140550813124160] Device[111] HT[1] DS[6729] TT[4.25] SNMP: v3: 10.10.2.1, dsname: apc_bankb1_near, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.6.1, value: 13
2024/05/13 14:13:01 - SPINE: Poller[1] PID[902208] PT[140550813124160] Device[111] HT[1] DS[6712] TT[3.54] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:12:31 - SPINE: Poller[1] PID[902121] PT[140341209269824] Device[111] HT[1] DS[6776] TT[8.75] SNMP: v3: 10.10.2.1, dsname: apc_single_overload, oid: .1.3.6.1.4.1.318.1.1.12.2.2.1.1.4.1, value: 24
2024/05/13 14:12:31 - SPINE: Poller[1] PID[902121] PT[140341209269824] Device[111] HT[1] DS[6728] TT[5.29] SNMP: v3: 10.10.2.1, dsname: apc_bankb1_low, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.5.1, value: 0
2024/05/13 14:12:31 - SPINE: Poller[1] PID[902121] PT[140341209269824] Device[111] HT[1] DS[6711] TT[4.70] SNMP: v3: 10.10.2.1, dsname: APC_line_voltage, oid: .1.3.6.1.4.1.318.1.1.26.6.3.1.6.1, value: 204
2024/05/13 14:12:31 - SPINE: Poller[1] PID[902121] PT[140341209269824] Device[111] HT[1] DS[6702] TT[3.98] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:12:01 - SPINE: Poller[1] PID[902046] PT[140479317608000] Device[111] HT[1] DS[6775] TT[2.46] SNMP: v3: 10.10.2.1, dsname: apc_single_near, oid: .1.3.6.1.4.1.318.1.1.12.2.2.1.1.3.1, value: 19
2024/05/13 14:12:01 - SPINE: Poller[1] PID[902046] PT[140479317608000] Device[111] HT[1] DS[6741] TT[13.62] SNMP: v3: 10.10.2.1, dsname: apc_total_overload, oid: .1.3.6.1.4.1.318.1.1.26.6.1.1.7.1, value: 24
2024/05/13 14:12:01 - SPINE: Poller[1] PID[902046] PT[140479317608000] Device[111] HT[1] DS[6727] TT[13.05] SNMP: v3: 10.10.2.1, dsname: apc_bankb1_load, oid: .1.3.6.1.4.1.318.1.1.26.8.3.1.5.1, value: 64
2024/05/13 14:12:01 - SPINE: Poller[1] PID[902046] PT[140479317608000] Device[111] HT[1] DS[6712] TT[10.84] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:12:01 - SPINE: Poller[1] PID[902046] PT[140479317608000] Device[111] HT[1] DS[6700] TT[10.02] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_overload, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.7.2, value: 16
2024/05/13 14:12:01 - SPINE: Poller[1] PID[902046] PT[140479317608000] Device[111] HT[1] DS[6699] TT[9.34] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_near, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.6.2, value: 13
2024/05/13 14:12:01 - SPINE: Poller[1] PID[902046] PT[140479317608000] Device[111] HT[1] DS[6697] TT[8.67] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_load, oid: .1.3.6.1.4.1.318.1.1.26.8.3.1.5.2, value: 106
2024/05/13 14:11:31 - SPINE: Poller[1] PID[901961] PT[140684880152128] Device[111] HT[1] DS[6774] TT[9.51] SNMP: v3: 10.10.2.1, dsname: apc_single_low, oid: .1.3.6.1.4.1.318.1.1.12.2.2.1.1.2.1, value: 0
2024/05/13 14:11:31 - SPINE: Poller[1] PID[901961] PT[140684880152128] Device[111] HT[1] DS[6740] TT[5.49] SNMP: v3: 10.10.2.1, dsname: apc_total_low, oid: .1.3.6.1.4.1.318.1.1.26.6.1.1.5.1, value: 0
2024/05/13 14:11:31 - SPINE: Poller[1] PID[901961] PT[140684880152128] Device[111] HT[1] DS[6702] TT[4.77] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:11:01 - SPINE: Poller[1] PID[901887] PT[139982698923584] Device[111] HT[1] DS[6739] TT[6.22] SNMP: v3: 10.10.2.1, dsname: apc_total_load, oid: .1.3.6.1.4.1.318.1.1.26.6.3.1.5.1, value: 169
2024/05/13 14:11:01 - SPINE: Poller[1] PID[901887] PT[139982698923584] Device[111] HT[1] DS[6712] TT[5.51] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:11:01 - SPINE: Poller[1] PID[901887] PT[139982698923584] Device[111] HT[1] DS[6698] TT[4.81] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_low, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.5.2, value: 0
2024/05/13 14:11:01 - SPINE: Poller[1] PID[901887] PT[139982698923584] Device[111] HT[1] DS[6696] TT[4.04] SNMP: v3: 10.10.2.1, dsname: apc_bankb1_overload, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.7.1, value: 16
2024/05/13 14:10:31 - SPINE: Poller[1] PID[901802] PT[139891495929408] Device[111] HT[1] DS[6738] TT[5.14] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_overload, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.7.2, value: 16
2024/05/13 14:10:31 - SPINE: Poller[1] PID[901802] PT[139891495929408] Device[111] HT[1] DS[6734] TT[4.45] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_overload, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.7.2, value: 16
2024/05/13 14:10:31 - SPINE: Poller[1] PID[901802] PT[139891495929408] Device[111] HT[1] DS[6702] TT[3.67] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:10:01 - SPINE: Poller[1] PID[901728] PT[140494898234944] Device[111] HT[1] DS[6737] TT[7.16] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_near, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.6.2, value: 13
2024/05/13 14:10:01 - SPINE: Poller[1] PID[901728] PT[140494898234944] Device[111] HT[1] DS[6733] TT[6.45] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_near, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.6.2, value: 13
2024/05/13 14:10:01 - SPINE: Poller[1] PID[901728] PT[140494898234944] Device[111] HT[1] DS[6712] TT[5.65] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:09:31 - SPINE: Poller[1] PID[901643] PT[139632126068288] Device[111] HT[1] DS[6736] TT[5.23] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_low, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.5.2, value: 0
2024/05/13 14:09:31 - SPINE: Poller[1] PID[901643] PT[139632126068288] Device[111] HT[1] DS[6732] TT[4.48] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_low, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.5.2, value: 0
2024/05/13 14:09:31 - SPINE: Poller[1] PID[901643] PT[139632126068288] Device[111] HT[1] DS[6702] TT[3.67] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:09:01 - SPINE: Poller[1] PID[901514] PT[139651844335168] Device[111] HT[1] DS[6735] TT[14.72] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_load, oid: .1.3.6.1.4.1.318.1.1.26.8.3.1.5.2, value: 103
2024/05/13 14:09:01 - SPINE: Poller[1] PID[901514] PT[139651844335168] Device[111] HT[1] DS[6731] TT[14.18] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_load, oid: .1.3.6.1.4.1.318.1.1.26.8.3.1.5.2, value: 103
2024/05/13 14:09:01 - SPINE: Poller[1] PID[901514] PT[139651844335168] Device[111] HT[1] DS[6712] TT[10.75] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:08:31 - SPINE: Poller[1] PID[901430] PT[139631500133952] Device[111] HT[1] DS[6730] TT[6.93] SNMP: v3: 10.10.2.1, dsname: apc_bankb1_overload, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.7.1, value: 16
2024/05/13 14:08:31 - SPINE: Poller[1] PID[901430] PT[139631500133952] Device[111] HT[1] DS[6702] TT[4.95] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:08:31 - SPINE: Poller[1] PID[901430] PT[139631500133952] Device[111] HT[1] DS[6695] TT[3.89] SNMP: v3: 10.10.2.1, dsname: apc_bankb1_near, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.6.1, value: 13
2024/05/13 14:08:01 - SPINE: Poller[1] PID[901357] PT[140520434103872] Device[111] HT[1] DS[6777] TT[23.31] SNMP: v3: 10.10.2.1, dsname: apc_single_load, oid: .1.3.6.1.4.1.318.1.1.12.2.3.1.1.2.1, value: 166
2024/05/13 14:08:01 - SPINE: Poller[1] PID[901357] PT[140520434103872] Device[111] HT[1] DS[6729] TT[9.50] SNMP: v3: 10.10.2.1, dsname: apc_bankb1_near, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.6.1, value: 13
2024/05/13 14:08:01 - SPINE: Poller[1] PID[901357] PT[140520434103872] Device[111] HT[1] DS[6712] TT[7.21] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:07:31 - SPINE: Poller[1] PID[901273] PT[139966785541696] Device[111] HT[1] DS[6776] TT[9.97] SNMP: v3: 10.10.2.1, dsname: apc_single_overload, oid: .1.3.6.1.4.1.318.1.1.12.2.2.1.1.4.1, value: 24
2024/05/13 14:07:31 - SPINE: Poller[1] PID[901273] PT[139966785541696] Device[111] HT[1] DS[6728] TT[5.74] SNMP: v3: 10.10.2.1, dsname: apc_bankb1_low, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.5.1, value: 0
2024/05/13 14:07:31 - SPINE: Poller[1] PID[901273] PT[139966785541696] Device[111] HT[1] DS[6711] TT[5.02] SNMP: v3: 10.10.2.1, dsname: APC_line_voltage, oid: .1.3.6.1.4.1.318.1.1.26.6.3.1.6.1, value: 204
2024/05/13 14:07:31 - SPINE: Poller[1] PID[901273] PT[139966785541696] Device[111] HT[1] DS[6702] TT[4.05] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:07:01 - SPINE: Poller[1] PID[901198] PT[140133497529920] Device[111] HT[1] DS[6775] TT[5.03] SNMP: v3: 10.10.2.1, dsname: apc_single_near, oid: .1.3.6.1.4.1.318.1.1.12.2.2.1.1.3.1, value: 19
2024/05/13 14:07:01 - SPINE: Poller[1] PID[901198] PT[140133497529920] Device[111] HT[1] DS[6741] TT[7.47] SNMP: v3: 10.10.2.1, dsname: apc_total_overload, oid: .1.3.6.1.4.1.318.1.1.26.6.1.1.7.1, value: 24
2024/05/13 14:07:01 - SPINE: Poller[1] PID[901198] PT[140133497529920] Device[111] HT[1] DS[6727] TT[6.96] SNMP: v3: 10.10.2.1, dsname: apc_bankb1_load, oid: .1.3.6.1.4.1.318.1.1.26.8.3.1.5.1, value: 66
2024/05/13 14:07:01 - SPINE: Poller[1] PID[901198] PT[140133497529920] Device[111] HT[1] DS[6712] TT[6.26] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:07:01 - SPINE: Poller[1] PID[901198] PT[140133497529920] Device[111] HT[1] DS[6700] TT[5.69] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_overload, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.7.2, value: 16
2024/05/13 14:07:01 - SPINE: Poller[1] PID[901198] PT[140133497529920] Device[111] HT[1] DS[6699] TT[5.10] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_near, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.6.2, value: 13
2024/05/13 14:07:01 - SPINE: Poller[1] PID[901198] PT[140133497529920] Device[111] HT[1] DS[6697] TT[4.39] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_load, oid: .1.3.6.1.4.1.318.1.1.26.8.3.1.5.2, value: 110
2024/05/13 14:06:31 - SPINE: Poller[1] PID[901113] PT[139734212228672] Device[111] HT[1] DS[6774] TT[8.73] SNMP: v3: 10.10.2.1, dsname: apc_single_low, oid: .1.3.6.1.4.1.318.1.1.12.2.2.1.1.2.1, value: 0
2024/05/13 14:06:31 - SPINE: Poller[1] PID[901113] PT[139734212228672] Device[111] HT[1] DS[6740] TT[4.36] SNMP: v3: 10.10.2.1, dsname: apc_total_low, oid: .1.3.6.1.4.1.318.1.1.26.6.1.1.5.1, value: 0
2024/05/13 14:06:31 - SPINE: Poller[1] PID[901113] PT[139734212228672] Device[111] HT[1] DS[6702] TT[3.58] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:06:01 - SPINE: Poller[1] PID[901039] PT[139893943522880] Device[111] HT[1] DS[6739] TT[6.16] SNMP: v3: 10.10.2.1, dsname: apc_total_load, oid: .1.3.6.1.4.1.318.1.1.26.6.3.1.5.1, value: 175
2024/05/13 14:06:01 - SPINE: Poller[1] PID[901039] PT[139893943522880] Device[111] HT[1] DS[6712] TT[5.52] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:06:01 - SPINE: Poller[1] PID[901039] PT[139893943522880] Device[111] HT[1] DS[6698] TT[4.88] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_low, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.5.2, value: 0
2024/05/13 14:06:01 - SPINE: Poller[1] PID[901039] PT[139893943522880] Device[111] HT[1] DS[6696] TT[4.16] SNMP: v3: 10.10.2.1, dsname: apc_bankb1_overload, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.7.1, value: 16
2024/05/13 14:05:31 - SPINE: Poller[1] PID[900955] PT[139913222329920] Device[111] HT[1] DS[6738] TT[5.08] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_overload, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.7.2, value: 16
2024/05/13 14:05:31 - SPINE: Poller[1] PID[900955] PT[139913222329920] Device[111] HT[1] DS[6734] TT[4.35] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_overload, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.7.2, value: 16
2024/05/13 14:05:31 - SPINE: Poller[1] PID[900955] PT[139913222329920] Device[111] HT[1] DS[6702] TT[3.34] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:05:01 - SPINE: Poller[1] PID[900879] PT[140494732473920] Device[111] HT[1] DS[6737] TT[4.91] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_near, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.6.2, value: 13
2024/05/13 14:05:01 - SPINE: Poller[1] PID[900879] PT[140494732473920] Device[111] HT[1] DS[6733] TT[4.17] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_near, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.6.2, value: 13
2024/05/13 14:05:01 - SPINE: Poller[1] PID[900879] PT[140494732473920] Device[111] HT[1] DS[6712] TT[3.38] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:04:31 - SPINE: Poller[1] PID[900791] PT[139987137955392] Device[111] HT[1] DS[6736] TT[5.29] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_low, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.5.2, value: 0
2024/05/13 14:04:31 - SPINE: Poller[1] PID[900791] PT[139987137955392] Device[111] HT[1] DS[6732] TT[4.33] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_low, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.5.2, value: 0
2024/05/13 14:04:31 - SPINE: Poller[1] PID[900791] PT[139987137955392] Device[111] HT[1] DS[6702] TT[3.42] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:04:01 - SPINE: Poller[1] PID[900717] PT[139964464047680] Device[111] HT[1] DS[6735] TT[5.61] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_load, oid: .1.3.6.1.4.1.318.1.1.26.8.3.1.5.2, value: 102
2024/05/13 14:04:01 - SPINE: Poller[1] PID[900717] PT[139964464047680] Device[111] HT[1] DS[6731] TT[4.87] SNMP: v3: 10.10.2.1, dsname: apc_bankb2_load, oid: .1.3.6.1.4.1.318.1.1.26.8.3.1.5.2, value: 102
2024/05/13 14:04:01 - SPINE: Poller[1] PID[900717] PT[139964464047680] Device[111] HT[1] DS[6712] TT[4.00] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:03:31 - SPINE: Poller[1] PID[900629] PT[140019659822656] Device[111] HT[1] DS[6730] TT[7.82] SNMP: v3: 10.10.2.1, dsname: apc_bankb1_overload, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.7.1, value: 16
2024/05/13 14:03:31 - SPINE: Poller[1] PID[900629] PT[140019659822656] Device[111] HT[1] DS[6702] TT[7.09] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:03:31 - SPINE: Poller[1] PID[900629] PT[140019659822656] Device[111] HT[1] DS[6695] TT[3.65] SNMP: v3: 10.10.2.1, dsname: apc_bankb1_near, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.6.1, value: 13
2024/05/13 14:03:01 - SPINE: Poller[1] PID[900556] PT[139850994079296] Device[111] HT[1] DS[6777] TT[7.79] SNMP: v3: 10.10.2.1, dsname: apc_single_load, oid: .1.3.6.1.4.1.318.1.1.12.2.3.1.1.2.1, value: 178
2024/05/13 14:03:01 - SPINE: Poller[1] PID[900556] PT[139850994079296] Device[111] HT[1] DS[6729] TT[4.69] SNMP: v3: 10.10.2.1, dsname: apc_bankb1_near, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.6.1, value: 13
2024/05/13 14:03:01 - SPINE: Poller[1] PID[900556] PT[139850994079296] Device[111] HT[1] DS[6712] TT[4.15] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:02:31 - SPINE: Poller[1] PID[900466] PT[140107817928256] Device[111] HT[1] DS[6776] TT[18.76] SNMP: v3: 10.10.2.1, dsname: apc_single_overload, oid: .1.3.6.1.4.1.318.1.1.12.2.2.1.1.4.1, value: 24
2024/05/13 14:02:31 - SPINE: Poller[1] PID[900466] PT[140107817928256] Device[111] HT[1] DS[6728] TT[5.12] SNMP: v3: 10.10.2.1, dsname: apc_bankb1_low, oid: .1.3.6.1.4.1.318.1.1.26.8.1.1.5.1, value: 0
2024/05/13 14:02:31 - SPINE: Poller[1] PID[900466] PT[140107817928256] Device[111] HT[1] DS[6711] TT[4.64] SNMP: v3: 10.10.2.1, dsname: APC_line_voltage, oid: .1.3.6.1.4.1.318.1.1.26.6.3.1.6.1, value: 204
2024/05/13 14:02:31 - SPINE: Poller[1] PID[900466] PT[140107817928256] Device[111] HT[1] DS[6702] TT[3.91] SNMP: v3: 10.10.2.1, dsname: APC_output_voltage, oid: .1.3.6.1.4.1.318.1.1.1.4.2.1.0, value: U
2024/05/13 14:02:01 - SPINE: Poller[1] PID[900392] PT[140386636965440] Device[111] HT[1] DS[6775] TT[11.05] SNMP: v3: 10.10.2.1, dsname: apc_single_near, oid: .1.3.6.1.4.1.318.1.1.12.2.2.1.1.3.1, value: 19
macan
Cacti Pro User
Posts: 898
Joined: Tue Mar 18, 2008 2:30 am
Location: Czech

Re: APC Metered PDU Data source value is showing in Last DS column. Value Column is showing NaN

Post by macan »

hmm, you got correct data:
2024/05/13 14:07:01 - SPINE: Poller[1] PID[901198] PT[140133497529920] Device[111] HT[1] DS[6727] TT[6.96] SNMP: v3: 10.10.2.1, dsname: apc_bankb1_load, oid: .1.3.6.1.4.1.318.1.1.26.8.3.1.5.1, value: 66

You can try create graph for this OID and use troubleshooting -> data sources
Let the Cacti grow!
kjstech
Cacti User
Posts: 97
Joined: Thu Feb 28, 2013 2:57 pm

Re: APC Metered PDU Data source value is showing in Last DS column. Value Column is showing NaN

Post by kjstech »

apc-graph-test.jpg
apc-graph-test.jpg (206.74 KiB) Viewed 170 times
I created a new graph, just one value and print the current, min, max and average. The value should be bankb1_load, which is a cdef divide by 10. See the data source troubleshooter = 67, so I should see 6.7 on my graph. If I get the data I can pretty it up and write Amps, but nothing loads on the graph. The rrd files create, this isnt a permissions problem.

RRDtool Command:
/usr/bin/rrdtool graph - \
--imgformat=PNG \
--start='1715694840' \
--end='1715695504' \
--pango-markup \
--title='APC PDU Stats' \
--slope-mode \
--base=1000 \
--height=150 \
--width=500 \
--alt-autoscale-max \
--lower-limit='0' \
COMMENT:"From 2024/05/14 09\:54\:00 To 2024/05/14 10\:05\:04\c" \
COMMENT:" \n" \
--color BACK#F3F3F3 \
--color CANVAS#FDFDFD \
--color SHADEA#CBCBCB \
--color SHADEB#999999 \
--color GRID#C4C4C4 \
--color MGRID#1A1C1C \
--color FONT#000000 \
--color AXIS#2C4D43 \
--color ARROW#2C4D43 \
--color FRAME#2C4D43 \
--border 1 \
--font TITLE:11:'Arial' \
--font AXIS:8:'Arial' \
--font LEGEND:8:'Courier' \
--font UNIT:8:'Arial' \
--font WATERMARK:6:'Arial' \
--slope-mode \
--watermark 'Generated by Cacti®' \
DEF:a='/var/www/html/cacti/rra/vfo_rack_1_pdu1_apc_bankb1_load_6778.rrd':'apc_bankb1_load':LAST \
CDEF:cdefa='a,10,/' \
AREA:cdefa#009F67FF: \
GPRINT:a:LAST:'Current%8.2lf %s' \
GPRINT:cdefa:MIN:'Min\:%8.2lf %s' \
GPRINT:cdefa:MAX:'Max\:%8.2lf %s' \
GPRINT:cdefa:AVERAGE:'Average\:%8.2lf %s\n'
RRDtool Command lengths = 1001 characters.
RRDtool Says:
OK

Graph exported to CSV

"Title","APC PDU Stats"
"Vertical Label",""
"Start Date","2024-05-14 10:05:00"
"End Date","2024-05-14 10:55:00"
"Step","1500"
"Total Rows","3"
"Graph ID","6768"
"Host ID","111"
""
"Date","col5-cdefa"
"2024-05-14 10:30:00","NaN"
"2024-05-14 10:55:00","NaN"
"2024-05-14 11:20:00","NaN"

Data Source Debug Mode:
OID
.1.3.6.1.4.1.318.1.1.26.8.3.1.5.1
Data Source Debug
/usr/bin/rrdtool create \
/var/www/html/cacti/rra/vfo_rack_1_pdu1_apc_bankb1_load_6778.rrd \
--start 0 --step 300 \
DS:apc_bankb1_load:GAUGE:120:0:U \
RRA:AVERAGE:0.5:30:800 \
RRA:AVERAGE:0.5:120:800 \
RRA:AVERAGE:0.5:5:23040 \
RRA:AVERAGE:0.5:1440:800 \
RRA:MIN:0.5:30:800 \
RRA:MIN:0.5:120:800 \
RRA:MIN:0.5:5:23040 \
RRA:MIN:0.5:1440:800 \
RRA:MAX:0.5:30:800 \
RRA:MAX:0.5:120:800 \
RRA:MAX:0.5:5:23040 \
RRA:MAX:0.5:1440:800 \
RRA:LAST:0.5:30:800 \
RRA:LAST:0.5:120:800 \
RRA:LAST:0.5:5:23040 \
RRA:LAST:0.5:1440:800 \
apc-bank-b1-load-data-source-info.jpg
apc-bank-b1-load-data-source-info.jpg (118.11 KiB) Viewed 168 times
APC - Metered PDU Multi-Bank B1 Load Data Source.jpg
APC - Metered PDU Multi-Bank B1 Load Data Source.jpg (223.11 KiB) Viewed 168 times
macan
Cacti Pro User
Posts: 898
Joined: Tue Mar 18, 2008 2:30 am
Location: Czech

Re: APC Metered PDU Data source value is showing in Last DS column. Value Column is showing NaN

Post by macan »

rrdtool dump /path_to/cacti/rra/...load_6778.rrd shows NaN on all lines?
Let the Cacti grow!
kjstech
Cacti User
Posts: 97
Joined: Thu Feb 28, 2013 2:57 pm

Re: APC Metered PDU Data source value is showing in Last DS column. Value Column is showing NaN

Post by kjstech »

Correct, heres a very small export of the wall of text that I get from that command somehwere in the middle of the file where things change a bit.
<?xml version="1.0" encoding="utf-8"?>
<!DOCTYPE rrd SYSTEM "https://oss.oetiker.ch/rrdtool/rrdtool.dtd">
<!-- Round Robin Database Dump -->
<rrd>
<version>0003</version>
<step>300</step> <!-- Seconds -->
<lastupdate>1715778271</lastupdate> <!-- 2024-05-15 09:04:31 EDT -->

<ds>
<name> apc_bankb1_load </name>
<type> GAUGE </type>
<minimal_heartbeat>120</minimal_heartbeat>
<min>0.0000000000e+00</min>
<max>NaN</max>

<!-- PDP Status -->
<last_ds>63</last_ds>
<value>NaN</value>
<unknown_sec> 271 </unknown_sec>
</ds>

<!-- Round Robin Archives -->
<rra>
<cf>AVERAGE</cf>
<pdp_per_row>30</pdp_per_row> <!-- 9000 seconds -->

<params>
<xff>5.0000000000e-01</xff>
</params>
<cdp_prep>
<ds>
<primary_value>NaN</primary_value>
<secondary_value>NaN</secondary_value>
<value>0.0000000000e+00</value>
<unknown_datapoints>0</unknown_datapoints>
</ds>
</cdp_prep>
<database>
<!-- 2024-02-22 02:30:00 EST / 1708587000 --> <row><v>NaN</v></row>
<!-- 2024-02-22 05:00:00 EST / 1708596000 --> <row><v>NaN</v></row>
<!-- 2024-02-22 07:30:00 EST / 1708605000 --> <row><v>NaN</v></row>
<!-- 2024-02-22 10:00:00 EST / 1708614000 --> <row><v>NaN</v></row>
<!-- 2024-02-22 12:30:00 EST / 1708623000 --> <row><v>NaN</v></row>
<!-- 2024-02-22 15:00:00 EST / 1708632000 --> <row><v>NaN</v></row>
...

<!-- 2024-05-14 15:05:00 EDT / 1715713500 --> <row><v>NaN</v></row>
<!-- 2024-05-14 15:30:00 EDT / 1715715000 --> <row><v>NaN</v></row>
<!-- 2024-05-14 15:55:00 EDT / 1715716500 --> <row><v>NaN</v></row>
<!-- 2024-05-14 16:20:00 EDT / 1715718000 --> <row><v>NaN</v></row>
<!-- 2024-05-14 16:45:00 EDT / 1715719500 --> <row><v>NaN</v></row>
<!-- 2024-05-14 17:10:00 EDT / 1715721000 --> <row><v>NaN</v></row>
<!-- 2024-05-14 17:35:00 EDT / 1715722500 --> <row><v>NaN</v></row>
<!-- 2024-05-14 18:00:00 EDT / 1715724000 --> <row><v>NaN</v></row>
<!-- 2024-05-14 18:25:00 EDT / 1715725500 --> <row><v>NaN</v></row>
<!-- 2024-05-14 18:50:00 EDT / 1715727000 --> <row><v>NaN</v></row>
<!-- 2024-05-14 19:15:00 EDT / 1715728500 --> <row><v>NaN</v></row>
<!-- 2024-05-14 19:40:00 EDT / 1715730000 --> <row><v>NaN</v></row>
<!-- 2024-05-14 20:05:00 EDT / 1715731500 --> <row><v>NaN</v></row>
<!-- 2024-05-14 20:30:00 EDT / 1715733000 --> <row><v>NaN</v></row>
<!-- 2024-05-14 20:55:00 EDT / 1715734500 --> <row><v>NaN</v></row>
<!-- 2024-05-14 21:20:00 EDT / 1715736000 --> <row><v>NaN</v></row>
<!-- 2024-05-14 21:45:00 EDT / 1715737500 --> <row><v>NaN</v></row>
<!-- 2024-05-14 22:10:00 EDT / 1715739000 --> <row><v>NaN</v></row>
<!-- 2024-05-14 22:35:00 EDT / 1715740500 --> <row><v>NaN</v></row>
<!-- 2024-05-14 23:00:00 EDT / 1715742000 --> <row><v>NaN</v></row>
<!-- 2024-05-14 23:25:00 EDT / 1715743500 --> <row><v>NaN</v></row>
<!-- 2024-05-14 23:50:00 EDT / 1715745000 --> <row><v>NaN</v></row>
<!-- 2024-05-15 00:15:00 EDT / 1715746500 --> <row><v>NaN</v></row>
<!-- 2024-05-15 00:40:00 EDT / 1715748000 --> <row><v>NaN</v></row>
<!-- 2024-05-15 01:05:00 EDT / 1715749500 --> <row><v>NaN</v></row>
<!-- 2024-05-15 01:30:00 EDT / 1715751000 --> <row><v>NaN</v></row>
<!-- 2024-05-15 01:55:00 EDT / 1715752500 --> <row><v>NaN</v></row>
<!-- 2024-05-15 02:20:00 EDT / 1715754000 --> <row><v>NaN</v></row>
<!-- 2024-05-15 02:45:00 EDT / 1715755500 --> <row><v>NaN</v></row>
<!-- 2024-05-15 03:10:00 EDT / 1715757000 --> <row><v>NaN</v></row>
<!-- 2024-05-15 03:35:00 EDT / 1715758500 --> <row><v>NaN</v></row>
<!-- 2024-05-15 04:00:00 EDT / 1715760000 --> <row><v>NaN</v></row>
<!-- 2024-05-15 04:25:00 EDT / 1715761500 --> <row><v>NaN</v></row>
<!-- 2024-05-15 04:50:00 EDT / 1715763000 --> <row><v>NaN</v></row>
<!-- 2024-05-15 05:15:00 EDT / 1715764500 --> <row><v>NaN</v></row>
<!-- 2024-05-15 05:40:00 EDT / 1715766000 --> <row><v>NaN</v></row>
<!-- 2024-05-15 06:05:00 EDT / 1715767500 --> <row><v>NaN</v></row>
<!-- 2024-05-15 06:30:00 EDT / 1715769000 --> <row><v>NaN</v></row>
<!-- 2024-05-15 06:55:00 EDT / 1715770500 --> <row><v>NaN</v></row>
<!-- 2024-05-15 07:20:00 EDT / 1715772000 --> <row><v>NaN</v></row>
<!-- 2024-05-15 07:45:00 EDT / 1715773500 --> <row><v>NaN</v></row>
<!-- 2024-05-15 08:10:00 EDT / 1715775000 --> <row><v>NaN</v></row>
<!-- 2024-05-15 08:35:00 EDT / 1715776500 --> <row><v>NaN</v></row>
<!-- 2024-05-15 09:00:00 EDT / 1715778000 --> <row><v>NaN</v></row>
</database>
</rra>
<rra>
<cf>LAST</cf>
<pdp_per_row>1440</pdp_per_row> <!-- 432000 seconds -->

<params>
<xff>5.0000000000e-01</xff>
</params>
<cdp_prep>
<ds>
<primary_value>0.0000000000e+00</primary_value>
<secondary_value>0.0000000000e+00</secondary_value>
<value>NaN</value>
<unknown_datapoints>1020</unknown_datapoints>
</ds>
</cdp_prep>
<database>
<!-- 2013-06-03 20:00:00 EDT / 1370304000 --> <row><v>NaN</v></row>
<!-- 2013-06-08 20:00:00 EDT / 1370736000 --> <row><v>NaN</v></row>
<!-- 2013-06-13 20:00:00 EDT / 1371168000 --> <row><v>NaN</v></row>
<!-- 2013-06-18 20:00:00 EDT / 1371600000 --> <row><v>NaN</v></row>
<!-- 2013-06-23 20:00:00 EDT / 1372032000 --> <row><v>NaN</v></row>
<!-- 2013-06-28 20:00:00 EDT / 1372464000 --> <row><v>NaN</v></row>
<!-- 2013-07-03 20:00:00 EDT / 1372896000 --> <row><v>NaN</v></row>
<!-- 2013-07-08 20:00:00 EDT / 1373328000 --> <row><v>NaN</v></row>
<!-- 2013-07-13 20:00:00 EDT / 1373760000 --> <row><v>NaN</v></row>
<!-- 2013-07-18 20:00:00 EDT / 1374192000 --> <row><v>NaN</v></row>
<!-- 2013-07-23 20:00:00 EDT / 1374624000 --> <row><v>NaN</v></row>
<!-- 2013-07-28 20:00:00 EDT / 1375056000 --> <row><v>NaN</v></row>
<!-- 2013-08-02 20:00:00 EDT / 1375488000 --> <row><v>NaN</v></row>
<!-- 2013-08-07 20:00:00 EDT / 1375920000 --> <row><v>NaN</v></row>
<!-- 2013-08-12 20:00:00 EDT / 1376352000 --> <row><v>NaN</v></row>
<!-- 2013-08-17 20:00:00 EDT / 1376784000 --> <row><v>NaN</v></row>
<!-- 2013-08-22 20:00:00 EDT / 1377216000 --> <row><v>NaN</v></row>
<!-- 2013-08-27 20:00:00 EDT / 1377648000 --> <row><v>NaN</v></row>
<!-- 2013-09-01 20:00:00 EDT / 1378080000 --> <row><v>NaN</v></row>
<!-- 2013-09-06 20:00:00 EDT / 1378512000 --> <row><v>NaN</v></row>
<!-- 2013-09-11 20:00:00 EDT / 1378944000 --> <row><v>NaN</v></row>
<!-- 2013-09-16 20:00:00 EDT / 1379376000 --> <row><v>NaN</v></row>
<!-- 2013-09-21 20:00:00 EDT / 1379808000 --> <row><v>NaN</v></row>
<!-- 2013-09-26 20:00:00 EDT / 1380240000 --> <row><v>NaN</v></row>
<!-- 2013-10-01 20:00:00 EDT / 1380672000 --> <row><v>NaN</v></row>
<!-- 2013-10-06 20:00:00 EDT / 1381104000 --> <row><v>NaN</v></row>
<!-- 2013-10-11 20:00:00 EDT / 1381536000 --> <row><v>NaN</v></row>
<!-- 2013-10-16 20:00:00 EDT / 1381968000 --> <row><v>NaN</v></row>
<!-- 2013-10-21 20:00:00 EDT / 1382400000 --> <row><v>NaN</v></row>
<!-- 2013-10-26 20:00:00 EDT / 1382832000 --> <row><v>NaN</v></row>
<!-- 2013-10-31 20:00:00 EDT / 1383264000 --> <row><v>NaN</v></row>
<!-- 2013-11-05 19:00:00 EST / 1383696000 --> <row><v>NaN</v></row>
<!-- 2013-11-10 19:00:00 EST / 1384128000 --> <row><v>NaN</v></row>
<!-- 2013-11-15 19:00:00 EST / 1384560000 --> <row><v>NaN</v></row>
<!-- 2013-11-20 19:00:00 EST / 1384992000 --> <row><v>NaN</v></row>
<!-- 2013-11-25 19:00:00 EST / 1385424000 --> <row><v>NaN</v></row>
<!-- 2013-11-30 19:00:00 EST / 1385856000 --> <row><v>NaN</v></row>
<!-- 2013-12-05 19:00:00 EST / 1386288000 --> <row><v>NaN</v></row>
<!-- 2013-12-10 19:00:00 EST / 1386720000 --> <row><v>NaN</v></row>
<!-- 2013-12-15 19:00:00 EST / 1387152000 --> <row><v>NaN</v></row>
<!-- 2013-12-20 19:00:00 EST / 1387584000 --> <row><v>NaN</v></row>
<!-- 2013-12-25 19:00:00 EST / 1388016000 --> <row><v>NaN</v></row>
<!-- 2013-12-30 19:00:00 EST / 1388448000 --> <row><v>NaN</v></row>
<!-- 2014-01-04 19:00:00 EST / 1388880000 --> <row><v>NaN</v></row>
<!-- 2014-01-09 19:00:00 EST / 1389312000 --> <row><v>NaN</v></row>
<!-- 2014-01-14 19:00:00 EST / 1389744000 --> <row><v>NaN</v></row>
<!-- 2014-01-19 19:00:00 EST / 1390176000 --> <row><v>NaN</v></row>
<!-- 2014-01-24 19:00:00 EST / 1390608000 --> <row><v>NaN</v></row>
<!-- 2014-01-29 19:00:00 EST / 1391040000 --> <row><v>NaN</v></row>
<!-- 2014-02-03 19:00:00 EST / 1391472000 --> <row><v>NaN</v></row>
<!-- 2014-02-08 19:00:00 EST / 1391904000 --> <row><v>NaN</v></row>
<!-- 2014-02-13 19:00:00 EST / 1392336000 --> <row><v>NaN</v></row>
<!-- 2014-02-18 19:00:00 EST / 1392768000 --> <row><v>NaN</v></row>
<!-- 2014-02-23 19:00:00 EST / 1393200000 --> <row><v>NaN</v></row>
<!-- 2014-02-28 19:00:00 EST / 1393632000 --> <row><v>NaN</v></row>
<!-- 2014-03-05 19:00:00 EST / 1394064000 --> <row><v>NaN</v></row>
<!-- 2014-03-10 20:00:00 EDT / 1394496000 --> <row><v>NaN</v></row>
<!-- 2014-03-15 20:00:00 EDT / 1394928000 --> <row><v>NaN</v></row>
<!-- 2014-03-20 20:00:00 EDT / 1395360000 --> <row><v>NaN</v></row>
<!-- 2014-03-25 20:00:00 EDT / 1395792000 --> <row><v>NaN</v></row>
<!-- 2014-03-30 20:00:00 EDT / 1396224000 --> <row><v>NaN</v></row>
<!-- 2014-04-04 20:00:00 EDT / 1396656000 --> <row><v>NaN</v></row>
<!-- 2014-04-09 20:00:00 EDT / 1397088000 --> <row><v>NaN</v></row>
<!-- 2014-04-14 20:00:00 EDT / 1397520000 --> <row><v>NaN</v></row>
<!-- 2014-04-19 20:00:00 EDT / 1397952000 --> <row><v>NaN</v></row>
<!-- 2014-04-24 20:00:00 EDT / 1398384000 --> <row><v>NaN</v></row>
<!-- 2014-04-29 20:00:00 EDT / 1398816000 --> <row><v>NaN</v></row>
<!-- 2014-05-04 20:00:00 EDT / 1399248000 --> <row><v>NaN</v></row>
<!-- 2014-05-09 20:00:00 EDT / 1399680000 --> <row><v>NaN</v></row>
<!-- 2014-05-14 20:00:00 EDT / 1400112000 --> <row><v>NaN</v></row>
<!-- 2014-05-19 20:00:00 EDT / 1400544000 --> <row><v>NaN</v></row>
<!-- 2014-05-24 20:00:00 EDT / 1400976000 --> <row><v>NaN</v></row>
<!-- 2014-05-29 20:00:00 EDT / 1401408000 --> <row><v>NaN</v></row>
<!-- 2014-06-03 20:00:00 EDT / 1401840000 --> <row><v>NaN</v></row>
<!-- 2014-06-08 20:00:00 EDT / 1402272000 --> <row><v>NaN</v></row>
<!-- 2014-06-13 20:00:00 EDT / 1402704000 --> <row><v>NaN</v></row>
<!-- 2014-06-18 20:00:00 EDT / 1403136000 --> <row><v>NaN</v></row>
<!-- 2014-06-23 20:00:00 EDT / 1403568000 --> <row><v>NaN</v></row>

,,,,

<!-- 2024-02-21 19:00:00 EST / 1708560000 --> <row><v>NaN</v></row>
<!-- 2024-02-26 19:00:00 EST / 1708992000 --> <row><v>NaN</v></row>
<!-- 2024-03-02 19:00:00 EST / 1709424000 --> <row><v>NaN</v></row>
<!-- 2024-03-07 19:00:00 EST / 1709856000 --> <row><v>NaN</v></row>
<!-- 2024-03-12 20:00:00 EDT / 1710288000 --> <row><v>NaN</v></row>
<!-- 2024-03-17 20:00:00 EDT / 1710720000 --> <row><v>NaN</v></row>
<!-- 2024-03-22 20:00:00 EDT / 1711152000 --> <row><v>NaN</v></row>
<!-- 2024-03-27 20:00:00 EDT / 1711584000 --> <row><v>NaN</v></row>
<!-- 2024-04-01 20:00:00 EDT / 1712016000 --> <row><v>NaN</v></row>
<!-- 2024-04-06 20:00:00 EDT / 1712448000 --> <row><v>NaN</v></row>
<!-- 2024-04-11 20:00:00 EDT / 1712880000 --> <row><v>NaN</v></row>
<!-- 2024-04-16 20:00:00 EDT / 1713312000 --> <row><v>NaN</v></row>
<!-- 2024-04-21 20:00:00 EDT / 1713744000 --> <row><v>NaN</v></row>
<!-- 2024-04-26 20:00:00 EDT / 1714176000 --> <row><v>NaN</v></row>
<!-- 2024-05-01 20:00:00 EDT / 1714608000 --> <row><v>NaN</v></row>
<!-- 2024-05-06 20:00:00 EDT / 1715040000 --> <row><v>NaN</v></row>
<!-- 2024-05-11 20:00:00 EDT / 1715472000 --> <row><v>NaN</v></row>
</database>
</rra>
</rrd>
macan
Cacti Pro User
Posts: 898
Joined: Tue Mar 18, 2008 2:30 am
Location: Czech

Re: APC Metered PDU Data source value is showing in Last DS column. Value Column is showing NaN

Post by macan »

hmm, no idea why data are retrieved but not saved.
You can try delete all graphs, data sources, rebuild poller cache and try add device again.
Cacti version? cmd poller or spine? Spine version?
Let the Cacti grow!
kjstech
Cacti User
Posts: 97
Joined: Thu Feb 28, 2013 2:57 pm

Re: APC Metered PDU Data source value is showing in Last DS column. Value Column is showing NaN

Post by kjstech »

Ok I deleted all the above, and same issue. The actual real value shows up in the Last DS column and not the value column. Its there but in the wrong place. I wish there was some sort of transform or function / ability to plot the data in Last DS instead of Value. What does Last DS stand for? My best guess is Last Downstream? Like downstream data (from snmp)?

The poller is spine.
Cacti 1.2.24.

Maybe I can try changing the poller interval? It defaults to 5 minutes. I have another one that's 30 seconds. I dont know if that would do anything.
Post Reply

Who is online

Users browsing this forum: No registered users and 0 guests